"Since I already have two breaker boxes, I would just split the new 50 amp cable, direct half of it to the existing transfer switch and the other half to the second breaker box."Yes. (Each breaker box has a 30amp main breaker protecting the box,
non?) (I didn't realize you already had two breaker boxes, but it doesn't change anything)
"..if I was on generator power, I would have only half of the 50 amps available, i.e., the half that was wired to the transfer switch?Yes. If you want everything available all the time, you'll need a NEW TRANSFER SWITCH, NEW 50AMP BREAKER BOX, NEW (#6 instead of #10 SIZE) WIRING ON ALL THIS, and your generator probably isn't large enough to carry it all.
"But if I was hooked up to 50 amp shore power the second a/c which I would wire into the second breaker box would be able to run at the same time that the first a/c was running." Yes.
"If I was hooked up to a 30 amp shore supply, which breaker box would be supplied?" Only the box on the BLACK wire - the "original" box which is tied to the transfer switch and carries all the original outlets and appliances.
10-28-2007, 06:29 PM
Jim and TereThanks Gunner. We're camping at the KOA Little River Campground in the Great Smokey Mountains park this weekend. First time out for the Barth in almost 1 1/2 years. Everything works. Will tackle the wiring to 50 Amps this next week. Sounds like a simple and very inexpensive way to achieve what I want to. Thanks again.