Forums    Barth Upgrades and Improvements    Honda 3000EU generator install
Page 1 2 
Go to...
Start A New Topic
Search
Notify
Tools
Reply To This Topic
  
Honda 3000EU generator install
 Login now/Join our community
 
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted
Back in the Keys, I got the headers installed so I got around to finishing some other Barth projects. I started this one last summer.

I got sick of the old 7kW Kohler klanker. Loud, heavy, vibrates and guzzles gas, bigger than I'll ever need.

I have always liked Honda generators for the opposite reasons. Unfortunately, Honda no longer makes the water cooled 4kW RV generators they used to.

I decided to take a shot at modifying and installing an air cooled 3000 watt inverter generator. I wanted to keep it portable if possible so I can use it for other jobs. It is one of the most quiet generators you can find.

I had 3 concerns:
1. Mounting it in the tray
2. Providing adequate air circulation for cooling
3. Connecting to the remote control panel inside Barth

1. The Honda weighs 148 lbs including its own 12v starting battery. (The Kohler is 350 lbs) It fits easily into the compartment. I made a few minor changes to the platform and strapped it in. I put 2 wooden mounts with recesses for the rubber feet under the generator.

2. This generator pulls cooling air from below and exhausts it out the left side. Unfortunately, the exhaust is combined internally with the cooling air so I couldn't run a discrete exhaust system. I built a sheet metal plenum which attaches to the left side and directs the air out the existing grate in the generator compartment door. It is lightweight and easily removable if I use the generator somewhere else. In addition, I wired two 110v muffin fans and attached them to the grate (blowing out) for additional scavenging and cooling air.







3. I removed the side covering the control panel and intercepted the wires to the ignition switch. I brought them out the side so I can attach them to the remote harness from the Kohler. They will be connected to the harness with a detachable plug to retain portability. The Honda wires have different functions so I have to rewire the Kohler dash panel as well. I still have to finish the dash control hookup.








So far this works really well. The 3000 will run both ACs. It will run one AC on the "eco-throttle" setting, which allows the Honda to run at near idle when the AC is not cycling the compressor.

There are only 2 details left.

1. The Honda has its own gas tank. I considered plumbing the gas line from the Kohler to the Honda but it would make it less portable. Instead I think I will wire in a small fuel pump to manually fill the Honda tank with a short hose.

2. The Honda has a manual cable style choke. I will not be able to cold start it from inside until I rig a choke system. I could run a cable but that would compromise portability so I think I'll rig an electric system with a small solenoid to pull the choke in.

Vibration is nil and it is so quiet you can barely hear it running inside the coach! With engine or AC running you can't hear it at all. I have run it down the road and the AC is great. Fuel consumption is very low, the Kohler used as much fuel at idle as the Honda does wide open! So far this is a much better generator setup than before.


9708-M0037-37MM-01
"98" Monarch 37
Spartan MM, 6 spd Allison
Cummins 8.3 325+ hp
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 2/16
Captain Doom
Picture of Rusty
posted Hide Post
The 3000EU is actually quieter (outside) than my EV4020 liquid-cooled RV genset. Inside, mine's ~16db quieter than the Kohler Klunker; the only way I can tell it's running on the road is the pilot light. Fuel consumption is ~35% of the Kohler LPG.

You'll be very happy you made the switch!


Rusty


MilSpec AMG 6.5L TD 230HP; built-to-order by Peninsular Engines:  Hi-pop injectors, gear-driven camshaft, non-waste-gated, high-output turbo, 18:1 pistons.  Fuel economy increased by 15-20%, power, WOW!"StaRV II"

'94 28' Breakaway: MilSpec AMG 6.5L TD 230HP

Nelson and Chester, not-spoiled Golden Retrievers

Sometimes I think we're alone in the universe, and sometimes I think we're not.
In either case the idea is quite staggering.
- Arthur C. Clarke

It was a woman who drove me to drink, and I've been searching thirty years to find her and thank her - W. C. Fields
 
Posts: 7734 | Location: Brooker, FL, USA | Member Since: 09-08-2005Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 3/19
Picture of Mogan David
posted Hide Post
FANTASTIC
Well done, Steve.
You never cease to amaze me. confusion
 
Posts: 2005 | Location: Jackson, Michigan, USA | Member Since: 04-18-2004Reply With QuoteReport This Post
First Month Member
Supporting Member of Barthmobile.com 11/13
posted Hide Post
Great Job!

quote:
There are only 2 details left.

1. The Honda has its own gas tank. I considered plumbing the gas line from the Kohler to the Honda but it would make it less portable. Instead I think I will wire in a small fuel pump to manually fill the Honda tank with a short hose.


You will find this handy. I have always used the genset pump for filling mowers, trimmers, hole diggers, etc. I even had a timer for shutting it when it had filled a Jerry can.

quote:
2. The Honda has a manual cable style choke. I will not be able to cold start it from inside until I rig a choke system. I could run a cable but that would compromise portability so I think I'll rig an electric system with a small solenoid to pull the choke in.


There is a wireless remote start for that gen. Give it a Google


.

84 30T PeeThirty-Something, 502 powered
 
Posts: 6169 | Location: AZ Central Highlands | Member Since: 01-09-2001Reply With QuoteReport This Post
Picture of MJ56
posted Hide Post
How do you manage the connections back to the coach power system? Plug in shore cord? Transfer switch?

Any advice on Champion brand generators?

Thanks.
 
Posts: 84 | Location: NW IN | Member Since: 09-22-2013Reply With QuoteReport This Post
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted Hide Post
The 3000 is 120v only but so is the coach. There is a 30 amp socket next to the 20 amp plugs on the panel (you can't quite see it in the photo.)

I wired the appropriate plug (Leviton L0530P) to the existing coach wires and use it like a shore power cord. Thumbs Up
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted Hide Post
quote:
Originally posted by bill h:
There is a wireless remote start for that gen. Give it a Google


I saw that but they want about $180 for the kit. Since I already had the Kohler wires I balked but it would be nice to have the choke solenoid... I don't suppose it's available separately.
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 8/11
posted Hide Post
Great Job Steve, that is a perfect replacement solution for the ole generator. That is on my project list. My ole Onan generator needs to be replaced for all the reasons you pointed out. Having the Honda for other uses is a big bonus.

I have a smaller Honda EU2000 that we use occasionally at work, people have borrowed it for remote RV camping, it'll run anything that a small RV has including the AC unit. Honda Generators are the best out there for portability.
 
Posts: 259 | Location: SouthWest MI | Member Since: 08-12-2011Reply With QuoteReport This Post
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted Hide Post
The 2000 Honda is a great, quiet, portable generator. One of my friends has one, it helped me decide to go that route. The 3000 has electric start, main reason I went for that size. I would definitely recommend the Honda inverter generators, run quiet and strong. Thumbs Up


9708-M0037-37MM-01
"98" Monarch 37
Spartan MM, 6 spd Allison
Cummins 8.3 325+ hp
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Picture of Doug Smiley
posted Hide Post
....Remote start a Honda Generator??

like this>>>>> http://www.remotemonitoringsys...enerator_project.php


_________________________

The 82 MCC {by Barth}
is not an rv--
it is a Motor Coach!!


 
Posts: 2584 | Location: Nova Scotia | Member Since: 12-08-2006Reply With QuoteReport This Post
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted Hide Post
Very sophisticated remote internet controller. Also pricey! confusion

They removed the gas tank, disconnected the ignition switch and removed the choke cable so the generator is no longer portable or capable of starting with its own switch. These are costly concessions in my world.

The door lock solenoid for the electric choke looks like a good option for me. I would just switch it on with a momentary switch while cranking. It may be a bit tight fit when the tank is still there. I will report any further changes! mechanic


9708-M0037-37MM-01
"98" Monarch 37
Spartan MM, 6 spd Allison
Cummins 8.3 325+ hp
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 2/16
Captain Doom
Picture of Rusty
posted Hide Post
If there's a hobby shop nearby, get a Turtle model railroad switch motor ~$20. It has a lever for connecting a pushrod and 2 positions.


Rusty


MilSpec AMG 6.5L TD 230HP; built-to-order by Peninsular Engines:  Hi-pop injectors, gear-driven camshaft, non-waste-gated, high-output turbo, 18:1 pistons.  Fuel economy increased by 15-20%, power, WOW!"StaRV II"

'94 28' Breakaway: MilSpec AMG 6.5L TD 230HP

Nelson and Chester, not-spoiled Golden Retrievers

Sometimes I think we're alone in the universe, and sometimes I think we're not.
In either case the idea is quite staggering.
- Arthur C. Clarke

It was a woman who drove me to drink, and I've been searching thirty years to find her and thank her - W. C. Fields
 
Posts: 7734 | Location: Brooker, FL, USA | Member Since: 09-08-2005Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 9/16
Picture of Quinn
posted Hide Post
My Onan generator sat for a couple months without being run, now it won't start. My mechanic says it needs a new carburetor (2nd time!) and control panel, to the tune of $1,000.

Came across this thread and again am reminded that some of you (e.g. Steve VW) are crazy-town mechanically talented. Not I.

A couple of questions:
1. Is it really "expected" that these carburetors will stop working if they sit for a couple months? Bear in mind the carb was only a year old.

2. Other than the job on this thread, which would take me, oh, 15 YEARS to complete, are there any recommendations for a generator with similar properties as the Honda, but without all the retrofit shenanigans?


89 28' Regal
Quad Bunks
P-30 454
8906-3623-28C-B
 
Posts: 235 | Location: San Leandro, California | Member Since: 08-06-2014Reply With QuoteReport This Post
Official Barth Junkie
Supporting Member of Barthmobile.com 1/24
Picture of Steve VW
posted Hide Post
There is no reason a carb should be shot in one year. However, with today's gasoline sitting in warm climes for a year it could be full of crud.

Given mechanics charges nowdays it might be cheaper to replace rather than clean/rebuild. The Onan modules are high priced junk IMHO but they are the only suppliers I know of. Not impressed with Onan as a company.

$1000 still seems high... hmm

BillyT from this site runs an RV repair place. He is the largest Onan repair shop in the central south. See if you can PM or call him. He will give you straight choices.

Check for used generators, esp from RV salvage yards. Might get lucky.


9708-M0037-37MM-01
"98" Monarch 37
Spartan MM, 6 spd Allison
Cummins 8.3 325+ hp
 
Posts: 5156 | Location: Kalkaska, MI | Member Since: 02-04-2011Reply With QuoteReport This Post
Supporting Member of Barthmobile.com 3/23
Picture of Duane88
posted Hide Post
Quinn, my Onan sat for a few years, would not start, I disconnected the air filter shot a bit of starting fluid in the carburetor intake as I was turning it over. Other than a bunch of oil leaks I had to fix it now runs like a champ. If the P30 fuel tank is less than 25% full the generator will not get any gas. Good luck!


1971 24 ft Barth Continental
P30 chassis
350 engine
 
Posts: 2041 | Location: Clinton Iowa | Member Since: 04-02-2017Reply With QuoteReport This Post
  Powered by Social Strata Page 1 2  
 

    Forums    Barth Upgrades and Improvements    Honda 3000EU generator install

This website is dedicated to the Barth Custom Coach, their owners and those who admire this American made, quality crafted, motor coach.
We are committed to the history, preservation and restoration of the Barth Custom Coach.